We have 2x E2 Plus chargers. I guess you can call one the master, as that has the CT before the meter, and the other slave charger is in the same group, with no CT. We have 2 properties, that combined have ~21kW of panels, 16kW of inverters, and 57kWh of home batteries. All on the same grid connection.
For the most part is works pretty well, but I have noticed a bit quirky behaviour.
So right now, are getting 16kW off the roof, Solar diversion is active, but the split between the 2 chargers is uneven. The slave is doing 6.9kW, and the master is doing 4.6kW.
The 2 cars charging are an Atto 3 on the slave, and a Tesla M3P on the master.
I have also noticed that the Atto3 when it is fully charged, will periodically blip on charging for about a minute or so. If the Tesla is charging at 7kW, and we are also exporting at 5kW, so plenty of excess power. The master will still derate to 3.5kW, the slave will start charging at around 3.5kW. The master will take several minutes to recover back to 7kW after the Atto3 has stopped. At which point it may do another blip.
Even though we have plenty of excess export, that it didn’t need to dip. I hope this behaviour can be improved?
sigh Have to break this into 2 posts, due to some stupid 5 embed limit.
More broken behaviour with 2 chargers, getting very frustrated and displeased.
Firstly, attached screenshots of the app notification spam, from the BYD Atto 3 cycling the charger on every few minutes when fully charged. Occurs even when notifications are disabled in the app. I had to kill the permissions.
even bigger sigh Let me just photoshop these 6 screenshots into 1, to get round this stupid embed limit.
Then this morning, it appears that the fully charged Atto 3 on the second charger, confused the system and stopped the other charger from starting. Unplugging the second charger on the Atto 3, and the first charger started instantly.
So instead of it being the dream, low maintanence setup. It is almost no different to having 1 charger, and swapping it between vehicles. As we have to keep unplugging one car, to make the other car charge.
This sounds like the charge manager may still see the Atto as an active session during those periodic top-ups, rather than as charge-complete. If so, it could reserve a minimum allocation on that charger and delay the other one starting. Worth asking the hardware team to log the control-pilot/session state and allocated current on both units across one blip and the blocked start; that should show whether the slave is failing to report a finished state. If the app allows stopping the Atto session rather than unplugging, try that and see whether the second charger starts immediately.